16a built in microwave
Philip Couzens 20/11/2026 - 8.03 AM
My current built in microwave which is plugged in to a 13a socket has packed up. Replacements I've seen are mostly 16a hard wired. When I had the kitchen refitted, electrician installed a dedicated distribution board for all the appliances. Supply to this board is with 4.0mm cable. Im guessing all the cables from this are 2.5 twin and earth. If i have the socket changed to a 16a hard wire outlet would it be safe.
Are you a tradesperson and able to answer this question?
1 Answer
Darius
Rating: 5 out of 5
A 2.5mm² cable is likely to be suitable for a 16A microwave, but before replacing the 13A socket with a 16A hard-wired connection, you should check the cable capacity, fuse rating and circuit suitability.
Having a 4mm² supply cable alone does not guarantee that the circuit is safe for 16A.
Answered20 November 2026