Anonymous user 17/11/2026 - 3.58 PM

An issue following the replacement of a corroded bathroom mixer tap. Since the tap was replaced, the hot and cold water have been coming through inconsistently. Sometimes the hot tap runs cold, and sometimes it runs hot. We've also noticed that the pressure on our combi boiler has increased to 2.5 bar, whereas it was previously around 1–1.5 bar. Could the new mixer tap have been incorrectly fitted or caused a cross-connection between the hot and cold water supplies? Could this also be related to the increase in boiler pressure?

1 Answer

Vialtus Construction Ltd

No reviews yet

Reading
It sounds more like a boiler issue, are all the taps in your house running inconsistently or is it just this one? Your boiler seems pressure seems to be at mains water pressure which indicates that mains water is making its way into your heating circuit. Firstly make sure your filling loop is closed. If it is, you should get in touch with a heating engineer most likely to be heat exchanger or diverter valve related.
Answered17 November 2026