Boiler only works efficiently if H.W & C.H programme comes on at different times!

Anonymous user 23/02/2024 - 2.43 PM

We have a new house with a Ultracom 18hxi condensing boiler. When it is very cold the radiators don't seem to heat up enough and keep closing down. However, I discovered that if I turn off the H.W the radiators warm up. The plumber came back 3 times last winter and once before Christmas, he changed the pump to a more powerful one and then he put on a "diverter." When he left the radiators were lovely and warm (it was quite a mild day) but then I noticed he only had the C.H switch on and not the H.W. That's when I discovered they worked better without the H.W being on, so I have set the programmer for them to work independently of each other, but this dosen't seem right. I contacted the manufactuer for help but they replied for our plumber to contact their helpline which he already did last year, from our house on a premium rate number! Anyone know the reason for this problem? Really appreciate your time and advice....

Are you a tradesperson and able to answer this question?

2 Answers

Anderson Heating & Gas

Rating: 4.8 out of 5
Northampton
Faulty diverter valve or blocked secondry heatexchanger
Answered18 January 2013
1

Efficient Heating services

Rating: 5 out of 5
Hull
sounds like your cylinder is taking the flow away from your heating system when running together....you should have a restrictor valve (gate valve) on the return from your cylinder coil...you should turn this FULLY off then open it by 2 full turns...this should be sufficient to heat rads and cylinderat same time. :-)
Answered18 January 2013