Earth bonding to external gas meter within block of flats

Anonymous user 13/04/2026 - 8.05 AM

Following a boiler service, I've been advised my gas meter looks like it needs earthing. All the gas meters are housed together in a different part of the building. The electrical meters are also placed in a different part of the building. Can anyone advise what this would entail? Will it mean routing new wiring through someone else's flat? Or running it outside? I'm confused about the logistics.

Are you a tradesperson and able to answer this question?

5 Answers

SES CONTRACTORS

Rating: 5 out of 5
Plymouth
Should never go through another property. Needs to be run from your fuse box to the gas meter.
Answered7 April 2026
0

zeus' home electrics

Rating: 4.9 out of 5
Birmingham
It entails running a 10mm copper cable sheathed in green and yellow, between either the main earth terminal inside your DB (fuse box) or an MET located close to the DNOs metering equipment to the gas meter. This is for the provision of a fault path.
Answered7 April 2026
0

Anonymous user

This needs investigating, Its most likely already bonded but the Gas engineer hasn't found it. also has the gas engineer made sure its not plastic because if it is it wont need bonding
Answered10 April 2026
0

oss electrician

Rating: 5 out of 5
Woolwich, London
on this situation you have to hire a qualified electrician to investigate this problem..you cant go just with someones advice who its not qualified on this field..probably gas pipe its earthed but you cant see that..proper qualified electrician mya give you proper advice
Answered13 April 2026
0

Ventoux Electrics

Rating: 5 out of 5
Alton
Firstly have an Eicr ( Electrical installation condition report ) completed, the inspector will be able to test if it needs bonding, we do a test to see if it is an extraneous conductive part, if it is, this bonding is used to reduce the magnitude of an electric shock during a fault by trying to equalise the potential between exposed and extraneous conductive parts. It shouldn’t go through another flat. Basically it is is essential to have if needed, if unsure get it tested, you can have a look at the incoming water in flats( usually) if you see a lot of PVC blue pipes it may not be needed, but the inspector should still conduct a test ( this could be done on it’s own)to make sure it’s not required. Hope this helps.
Answered13 April 2026