Central Heating

Part H building regulations

Anonymous user 17/02/2026 - 7.58 AM

I have been told that the new regulations require a 40mm hi heat waste condensation pipe needed for the bolier venting outlet into the waste, however my new WBosh combi boiler is in the loft and I would to vent out of the gable end into the soil stack pipe, do I to use 40mm hot water pipe as it will be insulated?

Are you a tradesperson and able to answer this question?

2 Answers

Southside Heating and Plumbing

Rating: 5 out of 5
Edinburgh
If the condensate pipe is outside it needs to be at least 30mm, insulated and no longer than 3m. That said, if there’s a way to connect to the solid stack internally that will always be the preferred option.
Answered13 February 2026
0

YK Heating Services

Rating: 5 out of 5
Cambridge
For external condense pipes we use minimum 32mm pipes, if it’s internal then 21.5mm one will do the job.
Answered17 February 2026