Vaillant Boiler Pressure
Anonymous user 17/02/2026 - 7.58 AM
My Vaillant eco boiler when hot goes up to 2.7 bars and when cold it’s at 2.2 bars. Is that normal? How do I fix it?
Are you a tradesperson and able to answer this question?
5 Answers
Core Plumbing & Heating Solutions
Rating: 4.9 out of 5
Cold pressure should be around 1.5 bar. As the boiler heats up, the pressure will rise slightly — that’s normal.
2.7 bar is high, and the pressure relief valve opens at 3.0 bar, which can cause water discharge.
Best to have an engineer service the boiler and check the expansion vessel.
Answered28 January 2026
0
SSA PLUMBING & HEATING SOLUTIONS
Rating: 5 out of 5
Hi ideally your boiler should be sitting at around 1.1 bar on a cold heating system, when the heating is on the pressure will rise due to expansion from the water circulating around the radiators getting hotter, this will then decrease as the heating system cools back down, so in answer to your question this is perfectly normal operation for the boiler.
Answered2 February 2026
0
Southside Heating and Plumbing
Rating: 5 out of 5
Normal - however, you really don't want the pressure much above 1bar when cold. You're running the risk of setting off the pressure relief valve in the boiler which will drop the pressure down suddenly, but you're also putting more strain on your fittings increasing possibilities of leaks.
Answered5 February 2026
0
YK Heating Services
Rating: 5 out of 5
Vaillant usually recommends to keep it between 1.1 - 1.5 bar when the system is cold. Over pressure might break some parts in your boiler such as expansion vessel. Under pressure might cause your boiler stop working.
Answered17 February 2026