earth rod my earth test shows 10ohms should be 5 ohms or below iam have a new gas boiler t

david cliff 06/11/2025 - 8.02 AM

will a earth rod solve this or would need two or more

Are you a tradesperson and able to answer this question?

4 Answers

AWB Electrical Services

Rating: 4.9 out of 5
Baldock
Your first move should be to get your DNO to come out check your earth. Assuming you are on a TNS earth system they have an obligation to maintain the Earth. If you are on a TT adding more earth rods will lower your Ze earth reading.
Answered6 November 2025
0

Michael Finn Electrics

Rating: 5 out of 5
Putney, London
Hi, 10 ohms is not bad for a TT system, the max permissible for a TT earthing arrangement is 200 ohms. You wouldn’t need to add anymore earth rods to comply. For a TN system though 10 is not good.
Answered6 November 2025
0

EV Charge Solutions

Rating: 5 out of 5
Kidderminster
Hi David, what is the purpose of this earth rod? If it is for your domestic properties electrical installation, a reading up to 200 ohms is acceptable.
Answered6 November 2025
0

Valley Core Electrical

Rating: 5 out of 5
Treharris
The max permitted external earth fault loop impedance of an earth rod on a TT system is 21 ohms. Although with RCD protection in place this can be raised to 1667 ohms
Answered6 November 2025