Connecting 4 core flex to bathroom fan’s 3 core flex.

Anonymous user 24/02/2024 - 2.30 PM

Hi, Our bathroom extractor fan is switched on by a light switch outside the bathroom, fed from a fused, 4 core socket spur. The fan switch is part of a double switch and the other switch switches on the bathroom light. So, the fan is operated independently of the light. The fan switch is connected to an old timer unit attached high on the wall outside of the bathroom. The fan has stopped working and I have disconnected it and tested it with a separate powered flex, to no avail. I have done a cursory check on the timer unit and there appears to be no voltage passing from the unit to the 3 core flex which goes through the wall to the fan. I can’t see any point to the timer unit as the fan has its own timer, factory set to 15 minutes. So, I would like to remove the timer unit and connect the 4 core flex to the 3 core flex. My question is, what is the safest way to wire the 4 core flex to the 3 core flex, without having a permanent live to the fan? Does the live from the 4 core go to the live connector in the fan terminal (existing setup) or Does the live from the 4 core go to the switched live connector in the fan terminal or Does the switched live from the 4 core go to the switched live connector in the fan terminal or Does the switched live from the 4 core go to the live connector in the fan terminal or Doesn’t it matter? Whichever way is best, either the live or switched live in the 4 core will be redundant and, I presume, should be blocked off? Thanks, Dan

Are you a tradesperson and able to answer this question?

4 Answers

Kirtek systems

Rating: 5 out of 5
Crawley
The fan as a timer set at 15 minutes it therefore needs both the live and the switched live connected. The switched live sets the over-run on the fan so once the switched live is turned off the fan runs for the 15 minutes set. You can link the switched & live in the fan on the switched live, but the fan will then only run when switched on with no timed over run. For the fan to run correctly as a timed unit it needs the four core cable run to the fan
Answered23 January 2024
6

Anonymous user

If you know the basics off this you shouldn’t be working at electric get a qualified electrician to come and install it to the regs
Answered3 February 2024
1

SVG Electrical Solutions Ltd

Rating: 5 out of 5
Andover
It seems like there is legacy cabling from a previous fan that didn't have an internal timer. Your best option is to get a qualified registered electrician to test the wiring installation of your fan. Part 7 Section 701 of the BS 7671:2018 Amendment 2:2022 covers locations containing a bath or shower.
Answered5 February 2024
0

Anonymous user

Completely over complicated from the start. If you know you know end of story
Answered5 February 2024