Swapping a faulty shower for a new one

Anonymous user 03/03/2024 - 3.47 PM

Hi. I’m about to remove existing shower which is rated at 9.5kw with a triton easy fit which is also rated at 9.5kw. It’s currently fed by 6mm twin and earth,length of run is probably only 5 metres. It’s got a 32A rcd via a double pole isolator.Is this acceptable or does the breaker need up rated?

Are you a tradesperson and able to answer this question?

5 Answers

SW20 Electrical

Rating: 5 out of 5
Raynes Park, London
Ideally it would be a 10mm cable on a 40a supply
Answered31 October 2023
2

Anonymous user

I would advise replacing the 6mm cable with a 10mm twin & earth
Answered31 October 2023
1

DMElectrical

Rating: 5 out of 5
Winchester
Remember to register it under part p with your scheme.... As it's required under law... You know, or else you'd be endangering folks, you are an electrician right?
Answered2 November 2023
1

Adrian Trofin

No reviews yet

Luton
Hi, per calculations, it is required to upgrade to 40a breaker and 10mm twin & earth.
Answered31 October 2023
0

Stellar Electrical & Energy Solutions

Rating: 5 out of 5
Dundee
Hi, I would advise upgrading to a 10mm twin and earth cable
Answered2 November 2023