Can i replace a double oven with a maximum load of 5285 to a 32amp breaker

Anonymous user 23/02/2024 - 3.52 PM

i would like to replace my old oven which ran off a 32amp breaker my new oven has a maximum load of 5285 would this be ok to swap

Are you a tradesperson and able to answer this question?

4 Answers

Butlers electrical LTD

Rating: 5 out of 5
Leighton Buzzard
Yes the oven will be okay to swap, assuming the 5285 is in watts the oven should draw 23A
Answered19 May 2023
10

Anonymous user

Yes that's fine. Ovens never draw their total rated load, load diversity is always applied.
Answered19 May 2023
0

A.K Electrical

Rating: 5 out of 5
Bristol
Assuming your supply is 230volts then Your oven maximum load is 5285Watts = 22.9A less diversity. I would recommend you change your 32A MCB/ROBO (Breaker) for a 20A to allow for the required disconnection time to be met
Answered20 May 2023
0

Correct Connections Electrical

Rating: 5 out of 5
Eastleigh
If that is the watts then you will be fine. Cookers rarely pull the maximum wattage anyway. They are thermostatically controlled which means they will switch in and out as and when required drawing small amounts of energy once temperature is reached. Apart from Xmas day I'm sure you will never be reaching anywhere near the maximum capacity.
Answered4 June 2023