Anonymous user 01/03/2024 - 3.00 PM

Hello, I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own supply with a 10mm Twin and Earth and the MBC is 32amps Can you please advise if the following Cable size is sufficient ( behind plaster ) MCB Amp needed Thanks in advance

Are you a tradesperson and able to answer this question?

5 Answers

Anonymous user

Please call a qualified electrician for various reasons such as insulation resistance, and continuity of CPC tests on the wires prior to installation. Only on the theoretical side of calculations: 11.15kW divided by 230V gives 49A However, there's a formula called diversity of demand which is first 10A of rating plus 30% of remainder plus 5A. So 10A + (30% of 39A) + 5A = 27A so a 32A breaker is sufficient. But ,please do call a qualified electrician as they have appropriate MFT testers to ensure safety
Answered27 January 2023
2

Anonymous user

Hello and good day. The cable size is adequate as long as the length of run isn’t greater than 30mtrs. The size of MCB required would need to rated at 50amps. Ideally and if possible, I would split them onto two different circuits. Thank you
Answered27 January 2023
1

Woodingdean electrical services

No reviews yet

Brighton
Hi 11.15 kw = 48.32a. With allowable diversity this can be reduced to 21.50a so the cable is more than capable of handling the load and a 32a breaker is fine. I hope this helps. Jim
Answered27 January 2023
1

Switch Electric Services Limited

Rating: 4.9 out of 5
West Hendon, London
Hi, Cable size is good you can use power up to 50amps. Better keep both seprate circuit Thank you
Answered27 January 2023
1

Total Trip Electrical Ltd

Rating: 5 out of 5
Newport, Shropshire
Both oven and induction hope should be in their own feeds with local isolators due to power requirements. 10mm twin and earth should be more than adequate however rating of cable depends on method of installation.
Answered27 January 2023