Connecting old footing to new footing for single storey rear extension

Anonymous user 23/02/2024 - 3.49 PM

Hi, Builder has excavated, BCO inspected and concrete poured in. Received SER calculations little late which shows new footing and old footing need connecting using duwell bars. Is there a way to fix this, more concerned now, if it was normal practice to use duwell bars nhbc approved builder he should have done it? Old and new footing both were at same depth at 1m. I spoke to builder today and he said he has put the bars before pouring. The day before pouring I had photos which didn't show any bars.

Are you a tradesperson and able to answer this question?

5 Answers

Anonymous user

Standard practice to join footings with bar. The only way I can see you doing it is to break out some concrete drill and resin the bars in and repour the concrete.
Answered14 October 2022
3

JD maintenance and construction.

Rating: 4.9 out of 5
Reading
It's standard practice when pouring new footings as an extension to drill into the existing footing and fix rebar so that when the new footings are poured they tie into the existing footings. Building control should have made sure this was known but to be honest your builder should have known this. I would say you'll have to cut/break out the newly poured concrete 1metre back from where it joins the existing footing drill and fix rebar to both old and new footings and pour concrete, however run it by building control first to keep them in the loop.
Answered16 October 2022
2

Anonymous user

They should have known and done it but it's not the biggest issue in the world to solve. I assume that the size and spacing of the dowels has been specified, if not, then just ask, they will be happy to let you know. Depending on the thickness of the original concrete, the dowels want to be at least 3" - 4" deep from the top. To put them in now, use an angle grinder and breaker to dig out the relevant amount of floor and then concrete in the dowel. In effect, you will be dove tailing the two floors together to look something like this. https://encrypted-tbn0.gstatic.com/images?q=tbn:ANd9GcR8c7vKeR0NkcQrCTh44NBgWHum7GS8_QlfgA&usqp=CAU
Answered14 October 2022
1

s & r brickwork and garden maintenance

Rating: 5 out of 5
Burgess Hill
Years ago we never put re bar into existing foundation so I wouldn't worry about it
Answered14 October 2022
1

Alex Williams

Rating: 5 out of 5
Ware
I have worked in quite a few extensions as a labourer, none have needed the bar, it might of been the structural engineer being keen
Answered15 October 2022