8-10 mm pipes and TRV’s

Anonymous user 23/02/2024 - 3.48 PM

We recently had a combi boiler installed from a standard boiler the pieces down stairs where 15 mm and upstairs 8-10 mm but the installer didn’t fit TRV upstairs saying that the pipes are rare??… is this true?

Are you a tradesperson and able to answer this question?

5 Answers

JL plumb ltd (JL Plumbing and Bathrooms)

Rating: 4.8 out of 5
Southampton
You can use elbow connectors which convert the 10mm to 1/2” /15mm which will connect straight on to the TRVs
Answered9 September 2022
0

Boiler Homecare

Rating: 5 out of 5
Honiton
If you start telling customers 'porky pies' you will always get found out. JL is correct
Answered9 September 2022
0

1st Class Gas

Rating: 5 out of 5
Glasgow
Remove 15mm olive and use a reducer olive in the TRV.
Answered11 September 2022
0

BSH Services

Rating: 5 out of 5
Accrington
10mm is quite common, 8 less so but you can still get the adapters to suit whether compression or solder. If they are 8mm though I would change them for 15mm, in fact depending on the size of radiators and how cold your house is I’d go to 15mm anyway. Hope this helps
Answered11 September 2022
0

24x7heatingEngineers

Rating: 4.9 out of 5
Manchester
You can always use reducer in the TRV of 15mm to adapt 10mm size pipework
Answered12 September 2022