Anonymous user 16/03/2024 - 2.47 PM

The water only gets lukewarm (18 degrees according to the boiler readout) even when the dial is set to maximum (65 degrees) . I can’t increase this no matter what temperature I set.

Are you a tradesperson and able to answer this question?

4 Answers

Anonymous user

if this is a vailliant ecotec plus 418. its most likely the flow switch
Answered8 June 2022
4

JRS plumbing and heating

No reviews yet

Glasgow
This could be a number of things. First I'd be looking at is the diverter valve or flow switch. Known issue with these boilers. If you run the hot water and the heating flow pipe at boiler gets hot the diverter will be your issue. Failing that, I'd Imagine a faulty flow sensor. You would know this if boiler doesn't light at all when running hot water
Answered8 June 2022
0

Anonymous user

Sounds like to me it could be the secondary plate heat exchanger is blocked.
Answered30 June 2022
0

Chesworth gas services ltd

Rating: 5 out of 5
Bootle
Needs to make clear make and model As if it’s a combi possibly a few different things but if it’s a 418 heat only then it’s a different fault all together
Answered4 July 2022
0