nest thermostat for systems boiler and multizone ufh

Anonymous user 03/03/2024 - 3.42 PM

Hi i am planning to install a system boiler with water based underfloor heating on all ground floor and raidators on first floor. UFH has 4 zones. Can i use nest thermostat with this system so 4 nest for 4 zones? Appreciate your help

Are you a tradesperson and able to answer this question?

4 Answers

Jonathan Andrews Plumbing & Heating

No reviews yet

Hayling Island
It would be better to set the radiator system and ufh system on seperate thermostats. Because they will heat up and cool at different rates.
Answered23 April 2022
5

MRB Gas and Heating

Rating: 5 out of 5
Milton Keynes
There is nothing wrong with using nests although rather costly for each of the zones but you should treat the radiator portion as a zone meaning you will need 5 thermostats, You can put thermostatic radiator valves on but you will still need some means of timing the so either a 5th nest or an separate programmer just for the radiators.
Answered25 April 2022
0

Cheshireheatingsolutions

Rating: 5 out of 5
Warrington
When you fit your ufh each zone will have a thermostat you need the electronic type which will work with most stats including the nest and hive very expensive to have them in every room but they will work
Answered12 May 2022
0

Martin House Plumbing Services

Rating: 4.8 out of 5
Lymington
Yes, that shouldn't be a problem but I would advise factoring it in at the design stage rather than afterwards to avoid any potential incompatibility issues. Also, as suggested in another answer, the 1st floor with radiators should be controlled by a Nest too. In all you will have 5 zones.
Answered19 May 2022