Underfloor heating in bathroom
Anonymous user 28/02/2024 - 4.03 PM
What are the regs for underfloor heating in the bathroom. Putting in a heating mat under tile area, wired to a thermostat outside, and electrician is asking me if the mat is suitable for bathroom. There is nothing I can see for any electric underfloor heating mat regarding IP44 rating and zones.
Are you a tradesperson and able to answer this question?
4 Answers
serica electrical
Rating: 5 out of 5
Just follow me manufacturers installation instructions. Just to be on the safe side keep the controller and power supply switches outside the bathroom. Regards, Andrew
Answered14 March 2022
2
Internal Repairs
Rating: 5 out of 5
Basically your electrician is right to query the ip rating of the floor mat. Most work in bathrooms requires more consideration as the bathroom is considered a 'special location'. Look it up.
Answered15 March 2022
0
Anonymous user
An underfloor heating mat is designed for underfloor heating in a bathroom. Thats probably the most common use for one. IP rating of floor mats indeed.
Answered17 March 2022
0
Daniel Morgan Electrical
Rating: 5 out of 5
Underfloor heating controls outside the bathroom on a switched fused spur, high up at 2m or low down at 450mm
Answered20 March 2022