Anonymous user 01/03/2024 - 2.55 PM

Hi all, I'm in a tight spot and would really appreciate help - I live in a new-ish (2009) flat. Hot water and central heating is provided by a recently fitted Worcester Greenstar combi boiler. Unfortunately, I've been having pressure drops both with the current boiler and the previous boiler over the span of a week. I'll refill the boiler to about 1 - 1.5bar, and it'll eventually drop to below .5bar, which will cause it to shut down. The central heating is a multi-zone underfloor system - no radiators at all in the property, so I can't visually confirm there's any leaks. Leak detection companies have told me that "the leak is so slow we wouldn't be able to find it" and to just keep an eye on it. I often check with my neighbours directly below and they haven't had any ingress that they can tell. My plumbers have confirmed the boiler is in good working order. This has been an issue for a long time now - and is especially bad during winter when I'll eventually wake up to a very cold flat that takes many hours to heat up after refilling the loop - let alone being able to rely on frost protection when away. What can I do next? I'm at my wits end!

Are you a tradesperson and able to answer this question?

4 Answers

T Murphy Plumbing

No reviews yet

Epsom
Ok so if you’re experiencing drops and there’s no sign of leaks on the heating system, then a possible way the system is dropping is through the pressure relief pipe. The pressure relief pipe is normally a discharge pipe leading to outside. Is there any signs of dampness around that pipe or on the wall is discharges at? Also another way the system could be dropping, is that overnight when your system is cold, the leaks tend to be more present.
Answered15 June 2021
4

PB Heating and electrical

Rating: 5 out of 5
Wigton
If your boiler expansion vessel and pressure relief valve are ok and the boiler is new then as a final check I would pressurise the system and isolate the heating circuit at the valves below the boiler for 24hrs. If the leak is in the heating system then the pressure should remain stable. If it still drops then issue is with the boiler. If it is confirmed as the system and the leak is small and no visible signs are apparent, then try adding a leak sealer from Sentinel or Fernox to the system, this may solve the issue.
Answered15 June 2021
1

JT Home Building Services

Rating: 5 out of 5
Hayle
I had this exact issue on my oil burner. When we moved in the heating was all over the place, when I checked the oil burner the last service person had left the device in TEST mode 😂😂 Make sure you boiler isn’t on TEST mode
Answered15 June 2021
0

Anonymous user

Though the information given is correct you should ask your heating engineer to check the pressure of your expansion tank in the boiler and any external expansion tanks
Answered25 June 2021