Would an electric combi boiler, cooker and shower exceed the 100amp power usual in houses?

Anonymous user 28/02/2024 - 2.53 PM

I am buying a house which only has electricity. I would like to fit an electric combi boiler, a cooker and an 8.5 electric shower. I've read a lot of the advice on this site and it seems the usual supply to houses is 100amps and these appliances might need a bigger power supply to the house. If so, how expensive is it likely to be? Thank you

Are you a tradesperson and able to answer this question?

2 Answers

Electrical Safety Services

Rating: 5 out of 5
Dereham
Really need to know the Kw rating of the electric boiler as they can be 16Kw or more. Allowing for diversity factors a 100amp supply should just about be ok, but if your planning to use all three at once then your could encounter problems. (Boiler 16Kw, Cooker 6Kw Shower 8.5Kw = 30.5Kw / 230volts = 132amps! Also this is not allowing for any load for other appliances, fridge, freezer, washing machine, lights etc. Getting a 3 phase supply installed will be several thousand pounds.
Answered28 June 2012
1

EXCELEC

Rating: 5 out of 5
Daventry
In a word, no, this is not too much power for a standard domestic property . Generally speaking, unless you are running a large number of appliances and generally consuming alot more than you generally would in a typical domestic situation then it would be necessary to get a 3 phase supply installed .
Answered25 June 2012