Epdm roof under coping stones

Anonymous user 09/03/2024 - 3.10 PM

Hi guys, I've built a single story extension with parapet walls and I was wondering how much of the epdm roofing sheet should sit on the top course (under coping stones) would it be roughly 40mm or would it sit on the full width of the internal course? (block) Also if I was doing this method where the epdm is running up the parapet wall and under the coping stone would I still need to use flashing if the internal wall is covered by epdm? Thanks

Are you a tradesperson and able to answer this question?

4 Answers

cameron loft and consruction ltd

Rating: 5 out of 5
Romford
Ideally 100 would be better but depending on the quality of bedding the coping stone pointed up etc 40 mm should be ok. No point using a lead cover flashing
Answered19 June 2020
8

Murf ltd

No reviews yet

Aylesford
No flashing. Edpm up an over Internal skin.
Answered19 June 2020
0

B.W.Construction

Rating: 4.8 out of 5
Congleton
You would need to board the backside of the parapit with 18mm osb board to just under coping stone for you to get a decent bond for the epdm as trying to glue straight onto bloc would be a nightmare make sure you go 100mm ontop of bloc work
Answered25 June 2020
0

Anonymous user

You should always provide a cavity tray under the coping stones (assuming it’s cavity). The EDPM would then lap over.
Answered11 July 2020