Hi guys had a leak on radiator so drained the system to fix all fixed now

Anonymous user 09/03/2024 - 3.09 PM

Hi leak fixed radiators are working fine all nice and hot. water coming out Of hot tap fine but no hot water at all after turning heating on for two hours . I have a condenser boiler with coppertank in loft and cold water tank above been told could b air block but have drained water out of tank with the same set up on end of radiator to release air but not had any out of pipes just a steady flow of water any help would b good thanks thanks davie

Are you a tradesperson and able to answer this question?

4 Answers

Wight Hot

Rating: 5 out of 5
Ventnor
Get an industry professional to do the work.
Answered20 April 2020
6

D & R Property and Plumbing Maintenance

Rating: 4.9 out of 5
New Romney
three way valve or zone valve problem either one not allowing heat from boiler into primary flow to cylinder,get a plumber or heating engineer to sort it out.
Answered20 April 2020
0

Anonymous user

You need to check your boiler and take out the air good luck.
Answered21 April 2020
0

DT Plumbing & Heating

Rating: 5 out of 5
Coalville
Agree with one of the answers above sounds like somethings not quite right with your zone valves your heating and hot water should be separate if you don’t have a combi boiler so should not interfere with each other.
Answered29 April 2020
0