RHP Twin pump allowing hot water to pass up the cold water feed?

Anonymous user 28/02/2024 - 3.48 PM

i have a RHP Twin pump connected but it appears that hot water is passing through the pump and up the cold water feed to the extent that the cold water tank is now warm? Should there be a balancing valve fitted?

Are you a tradesperson and able to answer this question?

4 Answers

D & R Property and Plumbing Maintenance

Rating: 4.9 out of 5
New Romney
you need to get a qualified plumber to sort this out for you.
Answered10 April 2020
7

Nigel Keen plumbing and heating

Rating: 5 out of 5
Nottingham
No you dont normally need a balancing valve It appears to me that the hot water pressure is higher therefore overriding the cold water pressure and moving up the cold pipe Best to run both pipes from the same tank if posdible and to run the same size pipes then you should have equal pressures
Answered10 April 2020
0

LLYN CAMBRIAN ELECTRICAL PLUMBING

Rating: 4.8 out of 5
Wrexham
If indeed water is being forced back into tank your overflow would be discharging water If it is not the warm water is being caused by something else Please advise to give a better reply
Answered13 April 2020
0

ADB Services UK Ltd

Rating: 4.9 out of 5
Moorgate, London
This is not a DIY Task as you could end up breaking the pump although. Engage a plumber locally