Is a 16amp Radial ok to power tumble dryer and dishwasher simultaneously

Anonymous user 15/03/2024 - 2.55 PM

I currently have a single socket fed from a 16 amp fuse on a radial socket feeding the dishwasher, I want to add a second single socket to feed a tumble dryer. When running both machines will i be ok on a 16 amp radial and 2.5mm T&E?

Are you a tradesperson and able to answer this question?

5 Answers

Anonymous user

An appliance runs on a 13amp fuse, therefore the max potential load is 26 amps. if both heaters energised simultaneously it would probably blow the 16 amp MCB
Answered22 March 2020
1

Anonymous user

Depends what the appliances both pull max load. Look at the wattage (kilowatt) in the manufacturer’s instruction manual. You could change the mcb to a 20amp which would allow you an extra 4 amps. 2.5mm cable is rated at 27amps so the mcb would trip at 20 amps protecting the cable way before it drew that load.
Answered25 March 2020
1

ROBERTO'S

Rating: 5 out of 5
Birmingham
my dishwasher and dryer are under a 13amp double socket on the ring and i never had any problems so you should be fine. worse case scenario your mcb will trip but both are not over 16amp.
Answered22 March 2020
0

DEACON ELECTRICAL SERVICES

Rating: 5 out of 5
Grimsby
Should be ok. You could change the 16 amp to a 20 amp.
Answered23 March 2020
0

Channell Electrics

Rating: 4.7 out of 5
Ashford, Kent
If the cable is 2.5 I would change the mcb to a 20 amp thus would comply
Answered24 March 2020