Hot taps in kitchen and utility room not triggering the Combi boiler

Anonymous user 15/03/2024 - 2.54 PM

Kitchen and utility room mixer taps have stopped triggering the boiler when hot taps turned on. Shower upstairs ( also mixer ) works for a while on hot but soon goes cold. Boiler has been checked by home services but they say it’s not a boiler issue. I’m not convinced!! The heating is working fine and radiators get hot as they should. This is happening on all the hot taps. They get hot but go cold after a short time. Taps further away from boiler not triggering it to fire up?

Are you a tradesperson and able to answer this question?

5 Answers

Jarek Jakiel

Rating: 5 out of 5
Sunbury On Thames
if problem is in one tap then that could be a issue, but if it happen in other places like shower mixer or basin tap means problem is in hot water distribution which is boiler, low water pressure may not turn boiler on or heat exchange in boiler not working properly
Answered23 February 2020
1

M. Sweet Building Contracter

Rating: 5 out of 5
High Peak
Could well be a problem with the in-coming water supply ! Sounds like there could be small amounts of trapped muck up to mains water tap !, therefore requiring re-placement of stop cock
Answered24 February 2020
0

Anonymous user

The problem could be the heat exchanger in the boiler . But it’s possible that 1 of the mixer taps is allowing the cold through which is usually at a higher pressure and can overpower the hot.
Answered24 February 2020
0

PHE London

No reviews yet

Staines
Hi. Is the boiler a Potterton performa? If so they have a very common issue with diaphragm switch. Could be that?
Answered25 February 2020
0

Huntingdon plumbing and plastering

Rating: 5 out of 5
Huntingdon
Could be she flow switch , temperature sensor or blocked plate heat exchanger
Answered26 February 2020
0