Flue reading analysis
I have a flue reading of 18.6 I am told it should be 20.9 and have been told flue seal leaking .. can you explain and confirm this information is correct please
5 Answers from MyBuilder Heating Engineers
Best Answer
West Drayton • Member since 1 Apr 2019 • No feedback yet
Yes this sounds correct. Sounds as if this is an analysis of the air intake to the flue which should ideally have an oxygen reading of around 20.9% or a minimum of 20.6% oxygen in air ratio/mix. As you state your reading is too low, this indicates the flue seals have perished and the air intake is mixing in the flue with the exhaust gases.. essentially starving the boiler of oxygen for combustion and will cause the boiler to burn incorrectly and be dangerous. I hope your engineer has capped of the appliance until this can be remedied. Some manufacturers allow the flue seals to be replaced.. however most of the time the whole flue needs changing.
Answered 27th Feb 2020
Port Talbot • Member since 10 Jul 2018 • 148 jobs, 99% positive feedback
I completely.agree with the reply given!
The boiler should be isolated from gas and a immediately dangerous notice issued with the users permission, if no permission given then the gas carrier should be informed about the findings
Answered 11th Mar 2020
Dewsbury • Member since 13 May 2014 • 443 jobs, 99% positive feedback
Hello
Mike Kitchen MT Gas & Heating
I too completely agree with the answer
The customer should be made aware of the problem and in the interests of safety the boiler should be capped, to be absolutely sure a new flue should be fitted to the boiler and new readings taken with the analyser to ensure the boiler is working effectively and safely
Answered 14th Mar 2020
Rotherham • Member since 14 Jan 2020 • No feedback yet
You need to be more specific with your details
Answered 22nd Feb 2020
Lytham St. Annes • Member since 8 Jul 2022 • 1 job, 100% positive feedback
Ive bought a new Kane FGA. Its reading 19.9 outside and 19.9 in the flue. Ive rang them as i had to get my m8 out with his fga and they said thats acceptable, i told them it wasnt and wanted it recalibrated. Is this acceptable?
Answered 19th Sep 2022
Related Questions
-
Valiant combination boiler
I had my boiler cut off due too carbon monoxide high level co2 reading of above 9.5 with a boiler ppm reading of 900 and a co/co2...
-
Flue inspection alternatives
Hi, I live in a flat that does not have inspection panels installed. I have been reading the gas safety website and come across...
-
boiler hissing/buzzing noise when it is about to shut down
Hi, I have a 5 year old potterton promax sl 15 boiler. The manual of which can be found at...
-
Gas Flue Analyser high reading
Could anyone shed any light on a possible cause of a high reading on a gas flue analyser. The reading being 1920ppm CO...

Post your job to find high quality tradespeople and get free quotes
Question Categories
- All Questions
- Architectural Services
- Bathroom Fitting
- Bricklaying
- Carpentry & Joinery
- Carpet & Lino
- Central Heating
- Chimneys & Fireplaces
- Conservatories
- Conversions - General
- Damp Proofing
- Demolition & Waste Clearance
- Driveways
- Electrical
- Extensions
- Fascias, Soffits & Guttering
- Fencing
- Gas Work
- Groundwork & Foundations
- Handyman
- Hard Flooring
- Insulation
- Kitchen Fitting
- Landscape Gardening
- Locksmiths
- Loft Conversions
- New Builds
- Painting & Decorating
- Plastering
- Plumbing
- Restoration & Refurbishment
- Roofing
- Security Systems
- Stonemasonry
- Tiling
- Tree Surgery
- Windows