Boiler runs 7 rads. Too many for it?
Anonymous user 15/03/2024 - 2.54 PM
Boiler runs 7 rads . Too many for it ? Gloworm engineer said he had set it up for 7/8 rads when he visited and it should be fine. Thoughts appreciated Thanks
Are you a tradesperson and able to answer this question?
6 Answers
D & R Property and Plumbing Maintenance
Rating: 4.9 out of 5
7/8 rads sounds ok for most combi boilers.
Answered29 January 2020
1
I Rae
No reviews yet
In a well serviced boiler 7 should be the minimum, depends on the output of the boiler and if it’s well maintained?
Answered29 January 2020
1
Anonymous user
May possibly need a secondary expansion vessel fitted.
Answered29 January 2020
1
Anonymous user
Depending on the size of the boiler and your rads 7 rads at 3kw =21kw so a 24kw boiler is fine any more heat out put from the rads and the boiler is undersized
Answered29 January 2020
1
Anonymous user
Hi, Even if we assume 1.5Kw per radiator as an average and say 3Kw for a cylinder if installed, you would have a 13.5Kw (10.5 rads/3 cylinder) demand. Even the smallest boiler would be able to cope with this, so in answer to your question, no 7 radiators is not too many as long as your boiler is over 13.5Kw which is fairly safe to assume. hope this helps.
Answered29 January 2020
1
Nestor Plumbing And Heating
Rating: 5 out of 5
Depending on the size of the radiators and kw of the boiler, but providing it’s been piped up correctly, then 7 rads shouldn’t be a problem at all
Answered29 January 2020