Skip to main content

Ready to hire?

Post your job in minutes, browse real reviews and choose who to speak to.Post a job

Need some tips or advice?

Ask a question
Gas Works

Biasi boiler fault ERR 04 with low pressure

Anonymous user 09/03/2024 - 3.05 PM

I’m having trouble with my boiler and I have no heating or hot water and constant error on screen. The pressure gage is low I need help !!! I don’t have a clue how to fix the issue. Any suggestions?

Are you a tradesperson and able to answer this question?

2 Answers

JB heating and plumbing solutions

Rating: 5 out of 5
Shoreham By Sea
Hi tammy you should have 2 isolation valves with a silver or grey flexible hose connecting the 2. This should be located close to the boiler either directly underneath or behind washing machine or dishwasher if they are located underneath the boiler. The isolation valves should have handles on that you turn to repressurise or a slotted one which you will need a screwdriver for. If you cant find this your boiler may well have a internal filling loop. Hope this helps
Answered17 November 2019
14

Mac Plumbing And Heating

Rating: 5 out of 5
Birmingham
I agree with JB heating. Please find your instruction manual if you have. Read it through there should be filling loop location if it built-in or manufacture provided. if not follow as Jb instruction.
Answered1 December 2019
0