8 Year old glow worm gaining pressure following service.
Anonymous user 03/03/2024 - 3.26 PM
Hello. I have a glow worm betacom prv is leaking even at normal 1.2/1.5 pressures....?
Are you a tradesperson and able to answer this question?
5 Answers
Trent Gas (Services) Ltd
Rating: 5 out of 5
I would presume the expansion vessel is deflated or burst
Answered12 November 2019
0
Peter J Brown Plumbing Gas & Oil
Rating: 5 out of 5
Vessel has been inflated with the pressure still on it, all the pressure should be dropped and then test/inflate the vessel to 1 bar then top system to 1.5bar
Answered12 November 2019
0
Anonymous user
Phone a Gas safe engineer
Answered12 November 2019
0
Anonymous user
Under pressurised expansion vessel is 100% the issue . Was this re pressurised during the service . If the gauge is constantly rising I would be looking at filling loop not closed fully .
If it was re pressurised during service was it done correctly. ( shut off f/r valves - pump vessel - drain vessel by prv . Once water removed re pressure exp vessel - open f/r valves then re pressurise boiler .
Answered12 November 2019
0
Gasworks Waterworks Ltd
No reviews yet
Expansion vessel requires servicing and PRV could need replacing if constantly leaking
Answered14 November 2019