8 Year old glow worm gaining pressure following service.

Anonymous user 03/03/2024 - 3.26 PM

Hello. I have a glow worm betacom prv is leaking even at normal 1.2/1.5 pressures....?

Are you a tradesperson and able to answer this question?

5 Answers

Trent Gas (Services) Ltd

Rating: 5 out of 5
Stoke On Trent
I would presume the expansion vessel is deflated or burst
Answered12 November 2019
0

Peter J Brown Plumbing Gas & Oil

Rating: 5 out of 5
Ayr
Vessel has been inflated with the pressure still on it, all the pressure should be dropped and then test/inflate the vessel to 1 bar then top system to 1.5bar
Answered12 November 2019
0

Anonymous user

Phone a Gas safe engineer
Answered12 November 2019
0

Anonymous user

Under pressurised expansion vessel is 100% the issue . Was this re pressurised during the service . If the gauge is constantly rising I would be looking at filling loop not closed fully . If it was re pressurised during service was it done correctly. ( shut off f/r valves - pump vessel - drain vessel by prv . Once water removed re pressure exp vessel - open f/r valves then re pressurise boiler .
Answered12 November 2019
0

Gasworks Waterworks Ltd

No reviews yet

Ardrossan
Expansion vessel requires servicing and PRV could need replacing if constantly leaking
Answered14 November 2019