Installing electric cooker
Anonymous user 09/03/2024 - 3.05 PM
Hi, I'm looking to purchase a new electric cooker. My old one is hardwired to a box and then wired up to the cooker switch which is a 32 amp fuse. The new cooker says that I requires to be hardwired to a 44.6 amp fuse and its electrical power rating is 10.7kw. The cooker has it's own breaker at the consumer unit rated at 32 amps. My question is do I just need to replace the 32 amp cooker switch to a 45 amp or does the breaker need to be changed to a higher amp as well along with the cabling?
Are you a tradesperson and able to answer this question?
5 Answers
MPC Electrical
Rating: 5 out of 5
Hello.
It all depends on the cable that's installed for it. The cable, the cooker switch and the breaker needs to be able to withstand 44.6 amps if that is the demand. Generally that will be a 10mm2 cable (depending on the run/grouping etc), a 45a isolator and a 45a MCB. You could potentially leave it as it is, but if the cooker draws more than 32a (so everything on the cooker is on) then it will trip the 32a breaker. Whatever you do, don't change the breaker without calculating whether the cable and isolator can take 45 amps.
Murray
Answered18 October 2019
16
BT ELECTRICAL SERVICES LTD
Rating: 4.9 out of 5
Yes, you need to change the Circuit breaker (fuse) to 45A. and check the cable if it is suitable to carry 45A current. 10mm2 cable would be suitable for 45A current load for any reference method used to erect the cable. if you have 6mm2 cable with reference method A (enclosed in conduit in thermally insulated wall) then you have to change replace the cable to 10mm2.
Answered18 October 2019
1
Anonymous user
https://www.tlc-direct.co.uk/Book/6.5.2.htm
Please see link... Which gives a 'fair' explaination on Diversity for cooker circuits...
It can only be calculated once all the power ratings are known... Then any good sparky will now what size cable to use. Contact me if more details are needed..
Regards,
Stephen
Answered31 October 2019
0
Evergreen Electrical Ltd
Rating: 5 out of 5
The diversity factor for domestic cooker goes like this:
45amps - 10 = 35amps x 30% =10.5 amps = the 10 you took of, = 20.5amps. That works well until Christmas morning, when everything is fired up!
Allowances for Diversity
The following table is typically used for when assessing the load of a group of circuits fed from a single distribution board or CU. Note that the total current value used is the total current after diversity has been applied - not just the nominal rating of the MCB or Fuse
Purpose of circuit Diversity applicable (domestic) Notes
Lighting 66% of total current
Heating and Power 100% of total demand up to 10A, + 50% of the remainder. Where space heating is connected to a general purpose power circuit.
Cooking appliances 100% of total demand up to 10A, + 30% of the remainder. Add a further 5A if a socket is fitted to the cooker point.
Water heaters (instant) 100% of first appliance, 100% of second, and 25% of any remaining appliances.
Water heaters (storage) No diversity allowable
Under floor heating No diversity allowable
Storage Heaters No diversity allowable
Standard Circuits 100% of current demand of largest circuit. + 40% of demand for every other circuit. These are standard final circuits as described in appendix 8 of the OSG
Answered4 November 2019
0
Anonymous user
Get an electrician round. Too many variables to consider for a lay person. Should prepare electrics prior to buying. Be prepared for a surprise moneywise.
Answered4 November 2019