6.2 KW oven fed by 2 x 2.5 twin and earth
Anonymous user 23/02/2024 - 3.26 PM
Can a 6.2KW oven be fed from a dedicated 32amp circuit protected by a 32amp mcb fed from 2 x 2.5mm twin and earth
Are you a tradesperson and able to answer this question?
8 Answers
POWERON
Rating: 5 out of 5
Hi there a 6.2kw oven draws 26.9 amps it is recommended to supply the oven with its own dedicated circuit with an isolation switch
Answered27 September 2019
2
Doctor Electric Ltd
Rating: 5 out of 5
Yes it can be connected, will it work? Yes, for a bit, then the cables will overheat which is dangerous, in the worst case it will cause a fire, so it isn't recommended.
Get an Electrician to run a bigger supply cable in from the Consumer Unit.
Answered27 September 2019
2
Anonymous user
If the 2.5 x 2 cables are just serving this appliance then it’s just a ring with a known fixed load. Absolutely no problem with that as a design. It’s an equivalent of a ring or could be classed as parallel conductors if they are the same length. It’s unorthodox but I can’t see any reason for it to be a departure from regs ?
Answered27 September 2019
1
SPRINGBUKS Group Services Ltd
Rating: 5 out of 5
Have an electrician determine the design requirements of the circuit and provide a quotation to provide that requirement.
Answered31 January 2021
1
PIA Properties and Maintenance LTD
Rating: 5 out of 5
I completely agree with Jon Bateson. There is no danger or departure from the regs, if the two cables are similar in length, terminated at the correct type isolator switch and definitely not serving anything else.
But I can also suspect that Coombes is trying to utilize an existing ring mains, so unless you blank off all sockets properly, stay away from this design.
Cheers
Ivan
Answered29 September 2019
1
Excelsior Engineering
Rating: 5 out of 5
In theory yes. But I’d say a big fat No. The problem with running parallel supplies is unless they are exactly the same length, the current will usually flow down the path of least resistance I.e. the shorter cable. Then this can lead to problems like overheating etc.
Answered30 September 2019
1
Anonymous user
Absolutely not. Sounds like you're trying to connect it to the ring main.
An oven should be supplied from its own dedicated protective device.
Answered27 September 2019