6.2KW DOUBLE OVEN FED FROM 2 X 2.5 TWIN & EARTH CABLES ON 32 AMP MCB
Anonymous user 23/02/2024 - 3.26 PM
CAN THE DOUBLE OVEN RATED AT 6.2KW AT 240V SUPPLY BE SUPPLIED BY 2 X 2.5 TWIN AND EARTH TOGETHER IN CONDUIT.
Are you a tradesperson and able to answer this question?
4 Answers
BRIAN SYKES ELECTRICIAN
Rating: 5 out of 5
It would appear the client is trying to connect a 6.2 KW oven to the ring main in the kitchen this is not advisable.
A fixed appliance IE ovens over 2KW should have a dedicated supply to allow for diversity factors over the ring main in the kitchen.
Answered27 September 2019
3
DEACON ELECTRICAL SERVICES
Rating: 5 out of 5
No. I’m amazed at the other answer saying yes you can
Answered27 September 2019
1
Steve Skelton Electrical Contracting Ltd
Rating: 5 out of 5
In theory yes as it’s similar to ringmain fused at 32A but it would be bad practice to do it that way. It should be a 6mm cable on a 32A MCB/RCBO with an isolator at the cooker.
Answered27 September 2019
1
Springs electric interiors ltd
Rating: 5 out of 5
Hi yes 2x2.5 twin and earth is fine to connect a 6.2 km cooker with 32amp mcb
Answered27 September 2019