Fitting lintel for new windows
Anonymous user 15/03/2024 - 2.49 PM
Do I need to fit a lintel both on the outer wall and the inner wall or will one be enough,
Are you a tradesperson and able to answer this question?
6 Answers
m horan brickwork specialist
Rating: 5 out of 5
One lintel will do. Make sure to allow for bearing That means the width of the window plus 150mm either side . So that means the width of the window plus 300mm equals the length of the lintel you will need. Get a prestressed one. One lintel will do so long as it covers the width of the wall. Michael.
Answered24 June 2019
2
Anonymous user
If your planning second stories A heavy duty Lintel.
Finishing of 1st level, above windows/Doors.
A cavity closure lintel
Spans both
Answered24 June 2019
0
LJB Lee Botting Ltd
Rating: 4.9 out of 5
The answer is yes. It’s the type of lintel in terms of strength, constructed into situ appearance and thermal abilities that are the real questions.
Answered24 June 2019
0
Anonymous user
Depending on the construction of the wall depends on what support is required ie a cavity wall requires both leaves supporting and a cavity tray inserting ,a traditional 9” wall requires support on the full 9” width of the wall normally 2 lintols or a reverse T lintol
Most lintol manufacturers have a great catalogue which shows which lintol can be used over differing construction of openings and if a heavy duty or special lintols would be required eg point loads or concrete floor construction above are just a few examples
Answered26 June 2019
0
W Scott Building Services
No reviews yet
If there’s masonry above the proposed window, on BOTH walls (or skins) then you will need a lintel on both walls or a steel “catnik” lintel which spans both walls and has its own damp tray so no DPM needed. Weep vents are still required. Catnik lintels allow for bricks, stone or a dressed stone or artificial stone head to be cemented ontop of it.
Answered26 June 2019
0
Anonymous user
If the wall is 9” thick and the exterior is a face work wall then you will require a box lintel
If you have a cavity wall and the exterior is facework then you will need a catnip lintel.
You will need a 150mm bearing each side I.e 1.200mm opening you would need a1.500mm lintel
Answered26 June 2019