So I have a 64amp Mcb in the garage , can I run and armoured to my shed and then protect it with a 32 amp RCD , the shed will only need 2 lights and 3 sockets for occasional use. I’m not doing the work myself but I want an idea so I know what to expect.

Are you a tradesperson and able to answer this question?

4 Answers

Anonymous user

The size of cable capable of carrying 64amps (25mm) would be way to big to run down to a shed for 2 lights and 3 sockets and the cost of that cable would be extortionate. If you do your cable calculations correctly you may be able to get away with a 6mm armoured or 10mm
Answered22 May 2019
5

DEACON ELECTRICAL SERVICES

Rating: 5 out of 5
Grimsby
Leave it up to the electrician who does it.
Answered22 May 2019
1

dminstallations

Rating: 4.9 out of 5
Garndolbenmaen
Firstly, you would be better putting a 32amp mcb in the garage to protect the SWA, which could then be sized for a 32a supply which depending on the cable length, might be 4mm or more, then a small consumer unit in the shed with perhaps a 20a and a 6a mcb to protect the socket and light circuits respectively, where you put the RCD is open to debate, but in the shed would be my choice
Answered5 June 2019
0

Martin Bryson Electrical

Rating: 5 out of 5
Motherwell
I would run a 10mm armour cable protected by a rcd it can carry a load 50amp fit a 2 way consumer unit in the garage with a 32 amp breaker for the sockets and 6amp for the lights a 25mm cable is to big for the job and the cost would be a lot more when you dont need a cable of that size
Answered6 June 2019