Immersion heater
Anonymous user 09/03/2024 - 3.00 PM
Some years ago I had a new bathroom installed requiring the rerouting of the 2.5mm immersion heater cable. I have discovered that the cable used by the electrician direct to the 3 KW immersion heater is not heat resistant type. Is it acceptable to run a length of 2.5 mm heat resistant cable from the immersion heater to a suitable junction box in the loft which is then connected to the existing cable. The existing cable from the distribution box is not accessible being under the floor.
Are you a tradesperson and able to answer this question?
2 Answers
EcoElectrical services
Rating: 5 out of 5
You need to fit a switched fused spur to the radial circuit & use butyl 3183TQ heat resistant flex from the fused spur to the immersion heater, hope this helps
Answered4 March 2019
0
Anonymous user
Personally I would only use a spur if immersion’s been fed from the ring. If it’s a dedicated radial on its own Mcb then I would use a 20a dp switch.
Answered4 March 2019