i connected a 2.5kw split ac onto old 32a cooker breaker circuit.. is this ok?
Anonymous user 15/03/2024 - 2.41 PM
I just installed a new hitachi 2.5 kw ac and wired it into an old cooker switch which goes to a breaker of 32amps. the unit https://www.aircon247.com/p/9062864/hitachi-summit-rak-25peb-25kw-inverter-split-wall-mounted-air-conditioning-system.html the unit works perfectly but the outdoor unit is making and electrical hum. did I do the wrong thing here??
Are you a tradesperson and able to answer this question?
2 Answers
DEACON ELECTRICAL SERVICES
Rating: 5 out of 5
Yes you did. Where is the fusing down etc.
Answered7 August 2018
0
Anonymous user
Fuses in consumer unit have to protect cable. so if Your old cooker outlet was protected by 32AMP breaker , cables for supply the cooker outlet will be 2x6sqmm+ earth.
You can connect to this outlet any appliance which not exceed 7.3kW so Your actual AC can be supplied from this line but to avoid any problems I recommend to exchange protecting device for MCB type B 16AMP
Answered9 August 2018