Oven/cooker installation - circuit shared with shower that's no longer in use

Anonymous user 28 February 2024 - 3.36 PM

Hi, we ordered a replacement built-in electric oven recently (to be hardwired in, replacing our current one that is also hardwired), but the installer refused to fit it because it is rated 16A rather than 40A as per the circuit breaker in our fuse box. He said we would either need to replace the circuit breaker with a 16A one or to order a 32A rated oven instead (strangely he told us that the 16A rating was really unusual for an oven, which turned out not to be true as we can barely find any new ovens rated at 32A - and even our current oven says 15-20A needed in the instructions!). Anyway, we have now had the circuit breaker replaced with a 16A one, which we assume will be fine in theory but there's an added complication in that the cooker circuit is shared with an old shower connection - said connection consisting of a standard wall socket added outside the bathroom, into which the old shower was plugged in (realise this is dodgy - was done by the previous owners, who did a lot of bad DIY!). We no longer have an electric shower at all, as the whole thing was removed when our bathroom was redone a while back - but are wondering if this shared circuit will cause an issue with regulations etc even if there is no longer any shower (given that the wall socket itself is still live so can in theory be switched on and things plugged into it). Would be very grateful for anyone's advice, as we don't want to get the installers back if they refuse to fit it again. You can probably tell we're clueless about all this - hadn't realised the issues until the fitters arrived! Thanks in advance. PS: new oven has a 3.65 kW power rating if that's relevant at all.

Are you a tradesperson and able to answer this question?

2 Answers

K.D.Marshall Electrical Services
Rating: 5 out of 5553 reviews
Westbury
Hi catclaires. In relation to your electric oven, a 16A MCB is ample for the KW rating of the appliance which will pull around 15.2 amps, however this is close to the limit of what the MCB will allow before it trips. Generally most electric ovens are ideally fed with a 6mm twin and Earth cable with a 20A MCB. In regards to the shared socket this ideally should be omitted due to the fact that if the oven is currently being used, anything that would be plugged in would likely trip the MCB due to an overload of the circuit if said appliance plugged into the shared socket would be using 1 amp or more. Taking off the socket face plate and replacing it with a blank plate would be a sufficed solution. I hope this helps, regards.
Answered13 March 2018
2

Anonymous user

Answer by K.D Marshall was spot on. I could only add that things like selecting a 6mm cable can only be done after also knowing things like the length of the cable run and how it is fitted in the house and whether is passes through/in any insulation material. However, in your case, if the circuit had a 32A breaker on it initially then hopefully you will be OK with a 16/20A one now. As always, if your not sure then get someone qualified to sort it, but at least this will give you some ideas of what to expect. Regards, Robin
Answered14 March 2018