Fire Alarm Requirements
Anonymous user 28/02/2024 - 3.36 PM
Hello, I have an apartment in a converted vicarage. The Fire Alarm is a hardwired mains installed system, with smoke detectors located in the communal areas and in each of the 5 apartments hallways. The apartment hallway is located off the main living room / kitchen and is not separated by a door (the smoke alarm being approx 3m from living room / kitchen). Am I required to have additional smoke/heat sensors put in the kitchens or is the current hard wired smoke alarm in the hallway sufficient?
Are you a tradesperson and able to answer this question?
2 Answers
K.D.Marshall Electrical Services
Rating: 5 out of 5
Hi, Mike, the regulations are that any living space i.e living room, bedrooms etc need a smoke detector within a maximum of 3m. In addition, the Regulations also require a heat alarm to be installed in any kitchen areas where the kitchen is not separated from the circulation space (hallways and landings) or stairways by a door. These alarms should also be mains powered with battery back up, so to put it simply yes you do need a heat detector in the kitchen as it not separated from the hallway by a door.
This of course is assuming that this is a new build.
Regards, Kasey.
Answered15 March 2018
0
Anonymous user
BS 5839 PARTS 1 & 6 state :
heat detectors should not be used within circulation areas , such a hallways,landing and corridors ( i.e. heat detectors should not to be used in any category LD3 of fire alarm system)
in category LD1 , LD2 and PD systems heat detectors may be installed within rooms in a dwelling, unless it is necessary to give the earliest possible warning of fire within the room
heat detector respond much more slowly than smoke detector but they are "steam/dust proof" and that is most common reason to install them in a kitchen area. because smoke detector installed in kitchen can react with steam during home baking or cooking.
going to the point is a good practice to have heat detector within 3 meters of " open fire place" like gas hob.. and requirement of Part B building regulations in NEW BUILD
Answered26 July 2018