13amp fuse for hot water cylinder

Anonymous user 03/03/2024 - 3.16 PM

Is a 13amp switched spur the correct fuse for a hot water cylinder with off peak and boost thermostats

Are you a tradesperson and able to answer this question?

2 Answers

DEACON ELECTRICAL SERVICES

Rating: 5 out of 5
Grimsby
Wouldn’t have thought so as an immersion heater will push a 13amp fuse to its limit, and eventually it will go. It’s usually wired by a dedicated supply from consumer unit on a 16 amp mcb then a double pole switch adjacent.
Answered18 December 2017
1

JEM ELECTRICAL CONTRACTORS LIMITED

Rating: 5 out of 5
Beccles
Nearly all Immersion heaters are rated at 3 kilowatt, this equates to just over 13amps. It doesn't mean the fuse will blow but good practice would be to install its own circuit direct from your consumer unit.
Answered19 December 2017
0