Urgent Ventilation advice needed please
Anonymous user 28/02/2024 - 3.31 PM
I'm just trying to confirm what type and how much ventilation is needed for my boiler. The boiler has been in place for over 30yrs and always inspected with no faults. Now we have bought the property and are told the boiler is at risk due to lack of ventilation. The boiler is an ideal w200 CF50 Gc 41429 18 The new person says we need high and low ventilation, but as I understand from the manual that's only the case if the boiler itself is in a cupboard
Are you a tradesperson and able to answer this question?
2 Answers
Boiler Homecare
Rating: 5 out of 5
If the boiler is located in an internal room/space that does not communicate directly with outside follow the following air ventilation requirement's:
High level: 170 centimetre's square
Low level: 340 centimetre's square
If the boiler is located in a room/space that has a suitable external wall that communicates directly with the outside then follow the following air ventilation requirement's:
High level: 85 centimetre's square
Low level: 170 centimetre's square
NB: Both the above air ventilation requirement's must be adhered to obviously if the boiler is within an internal room/space that does not communicate directly with atmosphere/outside also the air vents must be of a type that are NON-CLOSABLE AND FREE FROM ANY OBSTRUCTIONS AT ALL TIMES, such as furniture/book cases/shelving etc MOST IMPORTANT!
Strongly recommend that you fit a CO detector too near the boiler, follow the CO manufactures instructions when installing it!
Please ignore the post below regarding, ventilation
requirements, As you mentioned a boiler in a compartment or cupboard, there is no specific criteria that predefines the size/volume of a
'compartment' so data given above is from the manufacturers own specifications within there boiler installation manual. Please do not deviate!
Answered28 September 2017
0
Independent Central Heating ltd
Rating: 4.9 out of 5
If the boiler is in a room with an external wall (not in a compartment) you need only a low ventilation. You say you have the manual, the manufacturer tells you how big it has to be. For your boiler it should be about 65 cm2 of FREE ventilation (never ever cover the ventilation: you need the draft). It is very important for an open flue boiler (as yours) to be serviced once a year, and is good practice to have a carbon monoxide alarm as well.
Answered27 September 2017