Attic Radiator not working when other radiators in house are on.

Anonymous user 03/03/2024 - 2.44 PM

Radiator doesn't work when all the others in house are turned on (8 in total). When the other radiators are turned off the radiator does work and throws out loads of heat. As soon as I turn the others back on it goes off. Any other suggestions?

Are you a tradesperson and able to answer this question?

2 Answers

Your Plumbing

Rating: 5 out of 5
Prudhoe
Depending on the lift required from the boiler to the attic room radiator, you may need to upgrade your pump (to a 15-60 pump), but as sovereign rightly says, the system may just need balancing.
Answered6 December 2011
5

sovereign plumbing and heating

Rating: 5 out of 5
Walsall
water is idle and will always take the easiest route ,so you have to restrict the radiators closest to the boiler, you do this by turning down the radiators on the other side of the radiators ie opposite side from where you turn it off,grips and screwdriver necessary .warning it may cause these valves to leak slightly so think about calling an engineer, the process is called 'balancing'
Answered30 November 2011