Is there a law of what size cable can be put in for an electric cooker

Anonymous user 23/02/2024 - 3.09 PM

Got cooker electric double freestanding they won't fit as they say needs 10ml cable and mines 6ml I'm stuck now as can't find 6ml cable cooker anywhere. Hi thanks for that the cooker is 10.5kw Sally

Are you a tradesperson and able to answer this question?

2 Answers

DEACON ELECTRICAL SERVICES

Rating: 5 out of 5
Grimsby
Who is they? You can have a max load of 15kw on a 6mm cable with diversity applied and suitably sized protective device. What is the kw rating of your cooker in total? Your Edit. Well if it's 10.5 kw, then why can't it go on a 6mm cable. I would get a registered electrician in to do it who knows the electrical regulations BS7671 and can apply diversity to it from table A4 out of the on site guide which every electrician should have and get it done. 10mm cable is overkill. The only law that applies is the IET Electrical Regulations 17th Edition amendment 3 which is our bible really.
Answered16 May 2017
2

G Ratcliffe Electrical

Rating: 4.8 out of 5
Porth
Hiya what rating is the Electric cooker. Depending on the length of cable which in house hold circumstances is not normally long. 6mm put on a 40amp MCB this is in the region of 9KW.
Answered16 May 2017