New boiler - can i have a new boiler fitted if there is a a small gas leak?
Hi there,
Question – can I have a new boiler installed if there is a “small gas leak” but within the permissible drop? (Hope this makes sense as I am not quite sure I’ve got the terminology correct)
I was suppose to have a new boiler fitted last weekend but when the engineer tested the gas meter he said there was a 2 millibar drop. He said this is under the permissible drop of 4 millibar and I don’t need to have my gas switched off or call Transco. We were also not getting any gas smell so he said it is safe. However he said he cannot install the boiler as it is against regulation to have any pressure drop for a new boiler.
The engineer had checked both the internal pipes (one going to the kitchen for my cooker and the other going up to the loft for the boiler) and found that the small leak is in the pipe going into the kitchen). The engineer then recommended that I isolate the gas pipe going to the kitchen and do a new gas run or buy a new electric cooker.
I then called my internal gas pipe insurer and they sent someone round. After testing the gas meter the guy from the insurer said he could see that there is a drop of 1 millibar but this is totally safe as I am in an old properly and there is no smell of gas. The insurer is therefore not going to do anything and I cannot claim for reimbursement for a new gas run. The guy from the insurance company also said he can’t understand why the engineer couldn’t fit my boiler in as he would have done it without any issue as the drop was within permissible range. I also rang the Gas Safe Register and the impression they gave me was that it is fine to go ahead and install a new boiler because the drop is less than 4 millibar.
I am really confused as I do not understand why a new boiler cannot be fitted when the gas leak is within permissible drop and I can use all my current appliances safely? Is it true that a new boiler cannot be fitted in unless there is no drop?
Any advice or guidance will be very much appreciated as I do not want to putting in a new gas run if it is not necessary.
Thank you.
Regards
Michelle
10 Answers from MyBuilder Gas Engineers
Best Answer
clydebank plumbing and heating
Ashton Under Lyne • Member since 14 Apr 2011 • 33 jobs, 100% positive feedback
OK this is how it goes,and the only way it goes.You are not allowed any drop on the gas line at all if the engineer has isolated your gas appliances.There is a permissible allowance of up to 4mbr with appliances not isolated on the gas line,thats U6/G4 Meters E6 (Ultrasonic Meters) you are allowed up to 8mbr with old appliances connected,but if they are isolated from the gas line you are allowed no permissible drop.
Answered 21st Nov 2016
Margate • Member since 28 Apr 2017 • 12 jobs, 100% positive feedback
I would advise to replace the gas carcass when replacing the boiler, it seems pointless to leave a known drop on a carcass which with no smell is ok depending on which gas meter you have.
If it was my house or job I wouldn't be leaving a leak of any sort.
Answered 19th May 2019
Glasgow • Member since 18 Nov 2016 • 16 jobs, 81% positive feedback
Hi Michelle
This is a confusing regulation and can understand why it is mis-understood. You can have your new boiler fitted, the permissible drop is only allowed on existing pipework. Any new or altered pipework to the new boiler MUST be gas tight. This can be checked by leak detection fluid on all new joints and personally i would use a gas sniffer to be 100% happy.
Hope this helps.
Many thanks
Michael
Mower Development
Answered 18th Nov 2016
The Sussex Heating Care Company
Bognor Regis • Member since 6 Jul 2018 • 2 jobs, 100% positive feedback
The permissible drop is only relevant with all the appliances connected. If the appliances have been isolated (Gas cock to appliance turned off) and a tightness test has been carried out then there is no permissible drop and you have confirmed the leak is on the gas pipework so it should be repaired or replaced. You cannot use gas pipework knowing that it is leaking.
Answered 9th Mar 2019
Bolton • Member since 14 Sep 2015 • 94 jobs, 99% positive feedback
1mb drop per old gas appliance? I've never heard of that before.
In answer to your question, yes you can have a new boiler fitted onto a system which has less than 4mb drop providing there is NO smell of gas.
If there is currently a 2mb drop with not smell of gas, then after the new boiler is fitted there can only be the original 2mb drop.
Answered 26th Apr 2021
Newcastle Upon Tyne • Member since 13 Jun 2013 • 9 jobs, 100% positive feedback
All others are wrong!!!! Let me explain clearly.
You are allowed zero pressure drop on all gas pipe work.
You are allowed zero pressure drop on new gas appliance installation.
However you are allowed upto 1 mb drop PER OLD gas appliance like boiler, hob, fire etc individually. So if you have 1 old gas appliance your allowed 1mb drop etc etc.
Also if any gas pipes are lead, they have to be removed if work is being carried out on the gas line EVEN if the lead isn't causing the the leak.
Leaks dont get better over time, they get worse.
You house is worth zero pounds on the market with a gas leak and a life is priceless so get it sorted.
Theirs no such thing as acceptable gas leaks on the pipe work, only old appliances.
Answered 14th Dec 2020
Hook • Member since 11 Jun 2021 • 26 jobs, 100% positive feedback
There is no such thing as a permissable drop on a gas CARCASS. In short yes you could of had a new boiler fitted. However now the leak has been proven to be on the gas carcuss by disconnecting appliances no permissable, drop regardless of size or smell is permitted. I would call you insurer back as the supply has been tested with appliances disconnected and proved to be on the the carcuss. The supply needs to be capped and classed as immediately dangerous. Irrelevant of any smell of gas. Also a riddor should be raised against whomever is leaving your gas connected. Some of these answers are shockingly worrying on here.
Answered 20th Sep 2021
Workington • Member since 31 Dec 2020 • 4 jobs, 100% positive feedback
Get the "drop" sourced & repaired/disconnected using a gas safe registered engineer.
I personally would not start any gas work with a "drop"....permissable or not, present.
Answered 2nd Jan 2021
Norwich • Member since 19 Feb 2020 • 80 jobs, 100% positive feedback
I cant believe qualified gas engineers are saying that leaks are permissible....
Who in their right mind would want a leak anywhere,
Gas or Water!!!
Answered 1st Feb 2022
Ripon • Member since 24 Aug 2021 • 14 jobs, 86% positive feedback
Christopher plumber, obviously not a Gas engineer. If you were you would understand PERMISSABLE pressure drop, there is a reason for it which I don't have time to explain. QgH boiler repair from Bolton is 100%
Answered 8th Jun 2022
Related Questions
-
Is it a legal requirement to have a room themostat fitted with a new boiler/heating system?
Last summer we had a complete refurb of a house we'd just bought. This included replacing the old boiler and we now have a combi...
-
New boiler fitted on the benchmark it says system was flushed with TF3
Hiya thanks for reply on boiler that may need flushed. My argument is that I am aware of the pressure dropping is due to a leak....
-
Is there a minimum distance a gas cooker/hob needs to be away from wall-mounted boiler?
Hi all, I just purchased a flat in an ex-council building, and I'm looking to have the kitchen refitted. Right now the...
-
Do I need a type A RCD for a new boiler mains supply?
I have had a new boiler installed by British Gas. The old boiler was connected to the mains supply via a 13A plug into a standard...

Post your job to find high quality tradespeople and get free quotes
Question Categories
- All Questions
- Architectural Services
- Bathroom Fitting
- Bricklaying
- Carpentry & Joinery
- Carpet & Lino
- Central Heating
- Chimneys & Fireplaces
- Conservatories
- Conversions - General
- Damp Proofing
- Demolition & Waste Clearance
- Driveways
- Electrical
- Extensions
- Fascias, Soffits & Guttering
- Fencing
- Gas Work
- Groundwork & Foundations
- Handyman
- Hard Flooring
- Insulation
- Kitchen Fitting
- Landscape Gardening
- Locksmiths
- Loft Conversions
- New Builds
- Painting & Decorating
- Plastering
- Plumbing
- Restoration & Refurbishment
- Roofing
- Security Systems
- Stonemasonry
- Tiling
- Tree Surgery
- Windows