connecting a cooker to existing circuit

Anonymous user 15/03/2024 - 2.33 PM

I have to relace my free standing cooker.The existing circuit is from a 32amp mcb,type B.The unit is rcb protected.The cable is run to an isolator switch,about 18 ft run & then about 4 ft to the connection plate. I'm assuming that it is in 6mm cable but i don't know.The cooker will be 11kw total. If i'm correct in thinking that the circuit is in 6mm then i will probably be ok to use 6mm to connect. If i were to use 10mm cable from the cooker to the connection plate & the circuit is 6mm, would that be safe & vice versa.If the cooker circuit is in 10mm cable could i connect using 6mm cabe. Thanks for your reply.You are correct,my problem is that i don't know if the cable run is 6mm.How would i go about confirming that it is. If i rephrase the original question. If the cable from the consumer unit is by chance 10mm,( i've no reason to think that it is)before i do anything i'm just wondering if there would be a problem if i connected the cooker to the connection plate using 6mm cable. I don't have a problem making the connection but if there is a problem with different size cables, i would then get a electrician in to check the cable & make the connection. ----------------------------------------------------------------- Thanks for your reply.I've had to change the cooker due to actual width,I'm now looking at a 9.5kw total.I take on board your point about getting in a electrician because i'm not certain of the cable size. one last question if i may. I had a look at the online manual,see below. IMPORTANT: The following diameters of the supply cables must be used in the case of a one phase connection: Rated power on nameplate. Diameter of supply cable 9500w at 240v 3 x 4.0mm Is this correct ?connecting a 4mm cable to,in my case, a 6mm,possible 10mm power circuit. I also read somwhere, that the manufacturers connection instructions should be followed.

Are you a tradesperson and able to answer this question?

3 Answers

DEACON ELECTRICAL SERVICES

Rating: 5 out of 5
Grimsby
You can apply diversity to the cooker, which means you do not apply the total load in the calculation. The formula for working this out is In the IET wiring regs or the on site guide. why would you need a 10mm cable? If you don't quite know what you are doing i.e. don't know if it's a 6mm cable, i really do suggest hiring an electrician. The length of run of the cable is irrelevant in this case. Re your edit. I bet the instructions say also to be installed by an electrician etc. I will just repeat what I said before,as in, get an electrician in! The other answer you got was way off beam even for the original kw rating of the cooker you were going to get. As no diversity was applied. You are asking the same questions only in a different way. I am not going to tell you how to do it as I havnt seen it, this is hardly a DIY electrical job.
Answered8 October 2016
1

T&G Electrics

Rating: 5 out of 5
Tunbridge Wells
Hi, Your Cooker being 11Kw means about 40 amps, which would more than likely mean you will need a 10mm supply both from the fuseboard to isolation point - Isolation point to cooker connection and cooker connection to cooker itself with a 40 or 45a MCB in place at the fuseboard. If in doubt on cable size for sure get an electrician in to verify.
Answered6 October 2016
0

Gary lee electrical services and property maintenance

Rating: 5 out of 5
Clevedon
if you leave the 32amp breaker in place a 6mm cable is fine the worst that can happen is it will trip if the cooker draws to much, at 9.5kw you should be fine
Answered8 October 2016