How do I use a 3000w heat press on my home electricity without using a standard plug socket?

Anonymous user 23/02/2024 - 3.04 PM

I've recently bought a large format heat press (60cm x 100cm) and I'm having difficulties using it in my home studio. The heat press says it requires 3000w, 220v on the spec sheet. There's also a 40 amp glass fuse built into the machine. I've managed to get the heat press up to 180 degrees celcius once before the fuse blew using a standard british 13 amp plug but my main concern is that it's not safe to continue to use the machine this way as the plug socket heats up way too much and the fuse keeps blowing in the plug. My question is should I be running this machine on it's own dedicated circuit and not via plug sockets like an electric oven? And if so what would be the best set up to achieve this? Many thanks in advance

Are you a tradesperson and able to answer this question?

3 Answers

kevin cassidy building contractors

Rating: 5 out of 5
Accrington
3000w should run drawing 13A but being a heat press the draw is constant and for long periods at least until reaching temperature. Good practice dictates any appliance over 2000w be on a dedicated circuit. you don't say if the appliance is domestic or commercial. If domestic then a 2.5mm T+E radial protected by 16A breaker should suffice but if commercial I would lean to minimum 4mmT+E protected by 20A breaker. New circuits are notifiable to building control and easiest dealt with by registered electricians.
Answered3 August 2016
2

MJH Electrical Services Ltd

Rating: 5 out of 5
Bridgwater
Hi, Your best option is to wire it into its own dedicated 16a circuit straight from your consumer unit. 3000w is right on the limit of a 13a plug and that's why it could be blowing fuses. Always recommended to get a registered electrician to wire new circuits as n eeds to be notified to loacal authority. Hope this helps
Answered3 August 2016
0

Electrical Safety Services

Rating: 5 out of 5
Dereham
A 16amp industrial socket or even a BS1363 unfused 15Amp plug could be used but both will need a dedicated 16/20amp radial circuit installed, and preferably be RCD protected.
Answered3 August 2016