Anonymous user 09/03/2024 - 2.41 PM

Hi, I am not an electrician so please be gentle and I am fully aware I have been stupid trying to take on this work myself but I got let down by an electrician so ended up doing it myself as a plasterer was coming the day after. We just moved into a new house and the kitchen wiring looked shoddy at best, a lot of sockets needed moving etc. Even some exposed wires behind the kitchen cabinets (eek!) We have bought a 4.9kw double oven, a gas hob, and an extractor hood. There was an existing 10mm cable leading to an oven connection with a socket above it, I have wired that into a 20amp isolator switch, then from that switch there is a small length of 2.5mm wire going to a 13amp isolator switch. From the 20amp isolator there is a 2.5mm T&E cable which will eventually be installed into the oven. From the 13 amp isolator I am planning on wiring the extractor hood and the gas hob ignition over 2.5mm T&E. Is any of this safe whatsoever? I am planning on getting an electrician in to test it all but I am mainly worried about the 2.5mm wire feeding the 13amp isolator from the 20amp one (the 10mm feed cable and 2.5mm bridge cable are in the "in" connectors, and the cooker connector is in the "out" connectors on the isolator) And again, fully aware I am ridiculous for trying to do this myself! I am also unsure if its actually 10mm cable. Its definitely alot fatter than the 2.5 I have, like twice the width. Thanks in advance!

Are you a tradesperson and able to answer this question?

3 Answers

kevin cassidy building contractors

Rating: 5 out of 5
Accrington
Just where to start? 20A isolator too small. 2.5mm T+E feeding oven too small and ideally should be heat resistant flex usually stated in manufacturer instructions. (the 10mm T+E cable you mention is probably 6mm T+E) The set up you have sounds a bit of a mess so seriously recommend getting a registered electrician to sort it out as a matter of urgency for your own safety.
Answered3 August 2016
2

DEACON ELECTRICAL SERVICES

Rating: 5 out of 5
Grimsby
It's probably 6mm t&e and yes I would be worried as it sounds like you have spurred off a cooker circuit therefore the MCB/ fuse in the consumer unit is more of a rating than the 2.5 cable, etc etc etc. My feeling is the spark will fail it. good luck with it all
Answered3 August 2016
1

MJH Electrical Services Ltd

Rating: 5 out of 5
Bridgwater
Firstly what size protective device is protecting the 10mm? It needs to be a 32a. If it is a 32a or higher you should have put a 45a switch not a 20a. Then you should feed a 13a fused connection unit with a 6mm cable from the 45a switch. The cooker hood and gas ignition should then come from the load side of the 13a fused connection unit. Whilst the cooker should be wired from the load side of the 45a switch in a bit of 6mm cable. Hope this helps
Answered3 August 2016