Anonymous user 20/02/2024 - 2.30 PM

Are you a tradesperson and able to answer this question?

8 Answers

Anonymous user

Yes you can,the 17th regs says cables should be run verticaly or in safe zones you can also run horizontaly between two live points,in other words socket to socket.But as stated any work in a kitchen comes under Part P.
Answered7 March 2011
28

Anonymous user

This is not common practice as cables should always run vertically from ceiling or from floor.....yes it's behind tiling so know is going to try and knock a nail in the wall to hang a picture but if you ever sold the property and somenne for example put a spice rack up you would be liable and not being part p registered or an electrician will get you in a lot of trouble.
Answered7 March 2011
25

Anonymous user

Hello antiwaynrite, The current building regulations state.. "Where a cable is concealed in a wall or partition at a depth of less than 50mm from any surface it must be enclosed in earth metal conduit (trunking or cable) or installed either horizontally within 150mm of the top of the wall or patition or vertically within 150mm of the angle formed by two walls, or run horizontally or vertically to an accessory or consumer unit." ....."In dwellings, 30 mA RCD protection is required when a cable is installed in a wall or partition whose construction includes metal parts (fixings such as nails or screws are not included) and not protected by steel conduit or trunking or installed in a wall or partition at a depth of less than 50mm and not enclosed in steel conduit." for kitchens....."Socket outlets should be installed a minimum of 450 mm from the floor" ....."Accessories (sockets) should be installed a minimum of 300 mm from the edge of kitchen sinks and draining boards to reduce the risk of being splashed." etc etc etc. Adding socket-outlets and fused spurs to existing ring or radial circuits in a kitchen is required to be notified to Building Control. If you are using a registered competent firm, the certification body, on completion of the work, will notify Building Control for you. So under the existing regulations yes it is safe......................As long as you or your electrician know what you're doing and your Building Control Dept is notified. If in doubt.......dont! If you have to ask.......make sure you get the correct answer.
Answered9 March 2011
18

Anonymous user

Yes you can install cables horizontally between sockets. BS7671:2008 Regulation 522.6.6 (v) A cable concealed in a wall or partition at a depth of less than 50mm from a surface of the wall or partition shall be installed in a zone within 150mm from the top of the wall or partition or within 150mm of an angle formed by two adjoining walls or partitions. Where the cable is connected to a point, accessory or switchgear on any surface of the wall or partition, the cable may be installed in a zone either horizontally or vertically, to the point, accessory or switchgear. Where the location of the accessory, point or switchgear can be determined from the reverse side, a zone formed on one side of a wall of 100mm thickness or less or partition of 100mm thickness or less extends to the reverse side. Hope this helps.
Answered15 March 2011
16

Anonymous user

Its OK to run cables either vertically or horizontally but if at a depth of less than 50mm then the circuit MUST be protected by either an RCD or a RCBO.
Answered7 March 2011
9

Anonymous user

It is common knowledge for any tradesmen working in a kitchen that electrical cables should always run in straight vertical or horizontal lines from any sockets
Answered7 March 2011
7

V.A.Electrical services

Rating: 4.6 out of 5
Derby
Yes, you can do that if cable will run in safe zone ( horizontally at the same level as sockets)
Answered7 March 2011
6

Anonymous user

dont see why not , how often are you going to be drillinginto tiles in your kitchen
Answered7 March 2011
5