Will a 63amp rcd handle four high mcb?
Anonymous user 09/03/2024 - 2.38 PM
Is having four mcb on one 63amp rcd safe? I have three 32 mcb one running a 8.5kw shower and two being socket ring circuits and a 40 mcb for a 8.5kw shower on a single 63amp 30ma rcd. my consumer unit has a dual rcd both 63amp. One has all the higher output mcb and the other has the lower power mcb such as lights.
Are you a tradesperson and able to answer this question?
2 Answers
Proman Electrical Ltd
Rating: 5 out of 5
Hi,
This is a poor installation of the consumer unit, and as this has been done without any understanding, get the rest of the home tested and inspected.
The entire point of installing a dual RCD board is to split circuits for safety. So the lighting needs to be split as do the socket outlet circuits. Should you then have a fault on one circuit that trips the RCD, you only lose half of the lighting and sockets, this also means that you can easily detect that you have a problem.
Just adding up the value of the MCB's then comparing to the RCD is not correct. However, even allowing for diversity this does look a little unbalanced, so get it changed. You can't just swap the cables going into the MCB's. Find a registered electrician, ask him to do an EICR and swap the circuits around whilst he is there.
Answered11 April 2016
2
DEACON ELECTRICAL SERVICES
Rating: 5 out of 5
You, or preferably an electrician need to spread the loading over the two RCD's. Just a matter of swopping, and knowing what you are doing. Or perhaps you could swap one of the 63 amp for an 80 amp.
Answered8 April 2016