Pressure Fault F37 on a Otpimax 25C Combi Boiler

Anonymous user 01/03/2024 - 2.40 PM

Problem sorted now! Thanks for all your answers!

Are you a tradesperson and able to answer this question?

2 Answers

Pipe Dreams Plumbing Services

Rating: 5 out of 5
Bournemouth
Drain down your system until desired pressure using a Drain Off Valve on a Radiator by attaching a Hose Pipe to it. If you empty too much then you fill system upto required pressure using filling loop on or near boiler. Bill Pipe Dreams Plumbing Services Bournemouth#
Answered21 September 2011
0

clydebank plumbing and heating

Rating: 5 out of 5
Ashton Under Lyne
doubt it will be your bar pressure gauge!i would say that the water pressure switch is at fault,the problem is it is a wet pocket devise so you will have to empty the boiler!!!detach the wires and mark so they go back in the same way.the switch will cost you about £25ish.you see if the switch is faulty and it will go back to the board as far as the board is concerned it will regard the system as empty!!!tom cldebank plumbing&heating
Answered23 September 2011