I wish to install a 3.7kw instant water heater to a cloakroom basin can I connect it to a fused spur off the ring main or do I have go back to the consumer unit

2 Answers from MyBuilder Electricians

3.7kw is too high a load to connect to the ring, so yes a 20amp radial circuit will need to be run back to the distribution board. The circuit will need to be RCD protected as per BS7671:2008.

2015-07-27T17:35:02+01:00

Answered 27th Jul 2015

Need to go back to the consumer unit run a radial circuit with 20 amps circuit breaker at least (15amp will do as well) control by a fuse switch 15a as well,to be protected by rcd.

2017-10-18T20:15:01+01:00

Answered 18th Oct 2017