Hot radiators, but not water with system boiler

Anonymous user 23/02/2024 - 2.55 PM

Already the actuator zone valve, the 2 post valve body and the cylinder stat have been replaced. Now the engineer thinks that may be there is collection of sludge in a portion of hot water pipe and needs power flush. Do you agree that the problem is because of sludge or there could be some other cause?

Are you a tradesperson and able to answer this question?

3 Answers

Boiler Homecare

Rating: 5 out of 5
Honiton
Easy one to answer, call for hot water only, place your hand on the heating pipe leading directly to the top side connection of you hot water cylinder, does it begin to get warm? If so then check the bottom pipe (return) from the same cylinder, if that after a period of time is not becoming warm then you have proved that the hot water cylinder coil heat exchanger is preventing heat flow due to debris/sludge build up! Copy and paste link below in to your browser, as it illustrates your 'S' plan heating system and my above checking method: http://wiki.diyfaq.org.uk/index.php?title=File:S-Plan-Water.gif Please let us know how you get on?
Answered18 February 2015
3

FlameMaster Ltd

Rating: 5 out of 5
Llantwit Major
Could be , however , unlikely. I would suggest opening valve manually and feel with your hands if there is any difference in the surface pipe temperature of the uppermost pipe feeding the cylinder from the boiler. Most actuators have a manual operation facility , so this should be simple. If you operate the actuator and the pipe gets hot , this will indicate incorrect wiring of the controls/actuator. I came across a fault similar to this some time ago and found the expansion/breather pipe from the cylinder to the feed tank in the loft completely blocked - removed blockage - hot water restored. However , if you have water running freely at hot taps - whatever temperature - there is some form of impediment of the heating to the tank. There should also be an air vent at the uppermost heating feed to the tank - try venting this with actuator in manual operation.
Answered18 February 2015
1

Anonymous user

Firstly, check that you have a power supply to the 2 way zone valve when you have selected for hot water at the programmer, if so, check that the 2 port valve opens and closes when the cylinder stat is turned up and down. If these checks give positive results then I see 2 possible causes for no hot water. 1, air lock on the coil inside the cylinder. 2, partial blockage in the pipework between the 2 way valve and the return pipework common tee. If it's an air lock then selecting hot water only on the programmer and closing down the by pass valve might force feed and start working, if it turns out to be a blockage of sludge or debris, then a Powerflush is needed or to trace the blockage and remove manually to resolve. Hope this helps. Regards, Andy
Answered18 February 2015