Air sucked in through vent pipe on central heating

Anonymous user 23/02/2024 - 2.55 PM

I have an open vented system in which I recently changed the pump, even on the pump lowest setting air is being sucked in through the vent pipe. The setup looks like this: (please ignore the dots ) II . . . .vent into loft II. . . . II II . . . .II II . . . .II II . . . ..========== II . . . .II. . . . . . .II II. . . . II . . . . . .II II . . . .II . . . . . PP (pump into 3 way) II=====II cold . . II feed . .II There is about 1 metre between the cold feed tee and the pump tee (the pump is above cold tee), there was a block in the cold feed pipe which was replaced and drains freely ? Is this piping incorrect causing air to be sucked in ? Can this be fixed by moving the cold feed tee above the pump ? Any advice greatly appreciated. Thanks

Are you a tradesperson and able to answer this question?

2 Answers

Heat Central

Rating: 5 out of 5
Bewdley
Should be in this order Vent, Feed, Pump and within 150mm of each other. Common fault would be blocked cold feed usually where it tees into the flow/return. Can check with magnets have a google.
Answered28 January 2015
1

HD Design and Build

Rating: 5 out of 5
Herne Bay
Quality drawing!!
Answered29 January 2015